AndrewOG17

Structural
Joined
Jun 8, 2012
Messages
2
Location
US
I am analyzing a single plate shear connection with an axial load using AISC 13th edition. During my analysis I stumbled upon criteria 6 on page 10-103 which says "Ensure that the supported beam is braced at points of support" I am not sure what this is trying to say can anyone expound on this an give a better explanation.

Thanks,
 
Axial load in a single plate connection has an eccentricity. This must be considered in the connection design as a weak axis bending of the single plate. Unless the beam is restricted from lateral movement, by horizontal bracing, concrete, etc.

There have been several lengthy dicussions of this connection on this forum.

 
Seems like if you have a floor or roof deck laterally supporting the top flange, then that would be sufficient. Right?
 
If the distance "a" is less than 3.5" it wouldn't need to be laterally supported at bearing points would it? I would think since this criteria wasn't considered for the conventional configuration for "a" being less than 3.5" than you wouldn't need to worry about this. Or am I wrong for thinking that