I have the 6kVA Acme electric T-2A-53329-1S Transformer to install in a testing machine.
Like
Input is 480V 3ph. Three hots and Protective Earth ground.
Outputs will be 240V 3ph and of course readily available off that is 240V single phase and there is another tap for 120V 1ph.
I would add a pic of the wiring schematic but I don't see how to do that here.
My question is, in attaching to get 120V 1ph, it appears that we are tapping one end of a 240V winding and halfway down the winding, of course. Fine. BUT... it seems to me that neither of these wires will really be the usual "neutral"- that both wires will have a high voltage with respect to say the cabinet which is grounded. Therefor I worry that if a convenience outlet were installed for the machine operator, and wired to this 120V single phase tap.... both the outlet's terminals will be hot, and the only one with zero volts will be the ground terminal.
Or am I confused on this?
I have not had time yet to connect it to power and see if either end of the 120V tap has essentially N or Ground voltage.
If this can't be done because neither leg of the 120V tap is a viable Neutral, we can leave out the convenience outlet and just use the 120V 1ph for control and relay actuation within the enclosure. On the other hand if we need only use a 5-wire outlet and plug, in order to bring the building's Neutral in with the 3+1 power feed wires, that is a viable solution. Just a bit of guidance please.
Like
Input is 480V 3ph. Three hots and Protective Earth ground.
Outputs will be 240V 3ph and of course readily available off that is 240V single phase and there is another tap for 120V 1ph.
I would add a pic of the wiring schematic but I don't see how to do that here.
My question is, in attaching to get 120V 1ph, it appears that we are tapping one end of a 240V winding and halfway down the winding, of course. Fine. BUT... it seems to me that neither of these wires will really be the usual "neutral"- that both wires will have a high voltage with respect to say the cabinet which is grounded. Therefor I worry that if a convenience outlet were installed for the machine operator, and wired to this 120V single phase tap.... both the outlet's terminals will be hot, and the only one with zero volts will be the ground terminal.
Or am I confused on this?
I have not had time yet to connect it to power and see if either end of the 120V tap has essentially N or Ground voltage.
If this can't be done because neither leg of the 120V tap is a viable Neutral, we can leave out the convenience outlet and just use the 120V 1ph for control and relay actuation within the enclosure. On the other hand if we need only use a 5-wire outlet and plug, in order to bring the building's Neutral in with the 3+1 power feed wires, that is a viable solution. Just a bit of guidance please.