Thank you very much, Mike.
It looks like you are deriving the staple value from a diaphragm table as well, correct?. If I understood you right, you meant that a 180 plf value corresponded with 6" o.c. edge spacing. I think by your method, that would be 90 lb per staple, right? I think that would still need to be decreased by 33% per most diaphragm tables I have seen, based on the load duration assumed by the table, getting us to 67 lb.
Are you sure about that method? When you look at say a diaphragm for 8d commons @ 6" o.c. for 15/32" ply in DF, you get 260 plf. Your method would give the 8d a 130 lb value, then decreasing by 33% to get 98 lb. NDS nominal value for 8d in same conditions is 73 lb.
I found some other older engineering that gave a 53 lb. value to the same staple. That seems most reasonable to me so far.