Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Rupture Disk Outlet Pipe-Liquid

Status
Not open for further replies.

RJB32482

Chemical
Joined
Jan 19, 2005
Messages
271
Location
US
Hey Guys,
When sizing rupture disks with the coefficient of discharge method, what is the limit on the length and size of outlet pipe for liquid flow (certain % of pressure drop)?

Thanks.
 
I invite you to read my 6-part series on rupture disks found at
In this series I discuss why you don't want to use the coefficient of discharge method to do your rupture disk sizing. Briefly, this method does NOT directly take into account piping and its use is restricted to the
“8 & 5 Rule”. This rule states that in order to use this method to size the rupture disk ALL of the following four conditions MUST be met:

1. The rupture disk must be installed within 8 pipe diameters of the vessel or other overpressure source.
2. The rupture disk discharge pipe must not exceed 5 pipe diameters.
3. The rupture disk must discharge directly to atmosphere.
4. The inlet and outlet piping is at least the same nominal pipe size as the rupture disk.

There is no rule governing pressure loss other than the fact that you cannot exceed the relieving vessel's design pressure (or MAWP) plus allowable overpressure when the system is in relief.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top