robmaint:-
the type of connection you require is called a steinmetz connection. you connect the motor in delta (230 volt)and a 25mf 250 volt cotinuous capacitor is connected across 2 legs of the delta bridge, the supply (phase)is then applied to the 3rd leg and (neutral)to one lead of the capacitor.to reverse direction of rotation inter change neutral with capacitor leads.
note:- for a 0.25kw 4 pole motor new current will be 1.7 amps , eff 64% locked rotor current ratio 3, locked rotor torque 0.5 and pull out torque 2 x rated torque.
as motor now only developes 50% starting torque it may not excellerate the load. this type of connection is only good for centrificl fans and pumps.
hope this will help.
kind regds.