I think there was some decent discussion on there a while back on wind suction and whether it acts on "inside" or "outside" surfaces of a system. It seems to me that I was convinced by a sketch/general statics that all roof suction must be driven by a pressure difference (except maybe for the case of wind blowing up and under plys of roofing or something similar) and would act at the inside surface of a system. It may be worth a look back. Maybe there has been some recent code wording or publications that has convinced EZBuilding and bookowski.
I have not had to dig into this for a while, but am interested in what is decided. For roofing components like membranes, metal roofing, and possibly even sheet goods, I can see some local wind getting "up and under" components and casing separation of the system, but for something like a concrete topping layer, I see this as being much less likely. While it may be a good idea to adhere the layers nominally, designing this positive connection between layers for full wind uplift using low area C&C wind may not be completely necessary
Also - 200 psf uplift seems insane, even for 170mph exp D. I hope/assume that is an ultimate load. This is going to take alot of ballast to hold down. I hope the gravity resisting system will work for the "extra" concrete
I have done roofs with topping slab ballast to help limit uplift of the system, both with concrete and with "insulating concrete" . Ballast concrete was anchored to main structure in both cases, but I am not sure I was dealing with wind loads as high as you reference above.