Thank you for all the replies. Our original position was that AII Toilet Rooms are required to maintain negative pressure supported by at least 10 ACH computed on exhausted air. This position seems to be confirmed by an unofficial email I received on Friday from the ASHRAE 170 Chairman. The text of the email with my follow-up questions is below. Please feel free to continue this discussion. I value your input. (You might notice that my now italicized question was misunderstood to refer to the Main Room instead of the Toilet Room. I simply did not word the question well.)
ORIGINAL QUESTION BY WAY OF FGI WEBSITE FORM
The AIA ventilation table lists toilets as requiring 10 ACH at negative pressure. Is this for general toilets only? Does it also apply to toilets inside negative pressure isolation rooms? If not, is there no/any ACH requirement for toilets inside negative pressure isolation rooms?
If there is a requirement for ACH (10 or otherwise) inside negative pressure isolation rooms, is the ACH computed by the amount of exhaust in the toilet room? Does that change depending on whether there is a supply included inside the toilet?
Thanks for any quick guidance you can offer. I am having a discussion with a colleague and his client and we are interpreting the Guidelines differently.
ANSWER FROM FGI
Mr. Silverman:
I have forwarded your request to the chairman of ASHRAE 170 for response. I would anticipate a response from him shortly.
I have also included addenda "f" which addresses toilet and anterooms that are a part of the airborne infection isolation room. When it states directly opens onto an AIIR it does not mean without a door. It means without opening onto any other spaces.
Douglas S. Erickson, FASHE, CHFM, HFDP
Chair
Health Guidelines Revision Committee
ANSWER FROM ASHRAE 170 CHAIRMAN
I offer the following unofficial interpretation of Standard 170.
Questions are:
Q1. The AIA ventilation table lists toilets as requiring 10 ACH at negative pressure. Is this for general toilets only?
Response 1.
[li]No – this is not for general toilets only. The Table value for toilets apply to the toilet associated with the AII room.[/li]
Q2. Does it also apply to toilets inside negative pressure isolation rooms?
Response 2.
[li]The Table value for toilets apply to the toilet associated with the AII room.[/li]
Q3. If there is a requirement for ACH (10 or otherwise) inside negative pressure isolation rooms, is the ACH computed by the amount of exhaust in the toilet room?
Response 3.
[li]The Total ACH for the AII room is 12 ACH.[/li]
[li]Normally, the ACH for the AII room is calculated based on the air exhausting via the exhaust grille in the AII room.[/li]
[li]However, some of the 12 ACH could be provided by exhausting from the toilet and transferring air from the AII room.[/li]
Please note: the 10 ACH for the toilet will not be the same volume of air as 10 ACH in the AII room unless the toilet is the same size as the AII room.
My FOLLOW-UP
Thank you very much for your assistance. I have some follow up questions.
Q1. How does one get an official interpretation of a standard?
Q2. I understand exhaust from the Toilet Room inside an AII room can be used to achieve the required total of 12 ACH for the Main Room. Is my understanding correct? If so,
In the case of an AII room with a Toilet Room, should the total ACH for the Main Room be computed by combining the exhaust for both the Main Room and Toilet Room and dividing it by the volume of the Main Room and the volume of the Toilet Room?
ACH = 60(MRcfm + TRcfm) / MRvol + TRvol
Or, should the total ACH for the Main Room be computed by combining the exhaust for both the Main Room and Toilet Room and dividing it by the volume of the Main Room only?
ACH = 60(MRcfm + TRcfm) / MRvol
Or, is there yet another way it should be computed?