Repair of Concrete Roof
raystr2025
4
I have come across a problem in my project in which the concrete roof - the historical square rebar is exposed on the bottom face (only 3 of the 4 sides are in concrete).
We removed the terra cotta tiles that were originally there under this concrete roof, I guess they used the terra cotta as cover (?).
I asked the senior engineers in my office and one said to expose more deeper into the concrete
so they can expose rest of the faces of the square rebar and then form and pump the new concrete.
However I think creating chipping and creating pockets will undermine the structural integrity of the roof
(the historical loading for roof is D+L 1200 psf from 1905, today there is roadway above).
Is there a way to restore the concrete cover without disturbing any more of the roof or creating pockets on the sides to expose more of the rebar to form and pump?
The terracotta (hollow clay tile?) may be the form work. There are historic proprietary concrete systems that used the clay tile in a shallow vault to support the reinforced concrete fill. A web search might turn up a few examples that you could compare with what you've found.
Small areas of delamination might be repairable by chipping and grouting, but gravity will be working against you. For repairs of any magnitude proceed cautiously.
All the literature I’m aware of recommends getting the repair material up behind the bar, as your seniors have recommended. Simply shotcreting on a new layer doesn’t work; it’ll just delaminate off over time. You could protect the steel in other ways, like with cathodic protection. I’m with @Michel60; proceed cautiously.
Also you probably will want to sample and test the remaining concrete as well to ensure it's properties are even close to what is needed in terms of compressive strength, shear and bond strength, etc.
Below a roadway suggests maybe long term deterioration of the concrete via chlorides, etc. You might just have some powder up there.