I have a client who wants to move a 30ftx30ft PEMB elsewhere on his lot. The building is 11 years old. Also the PEMB manufacturer has since gone out of business.
IEBC CH 14 generally states, "Buildings shall comply with IBC provisions as applicable"
Does this mean that I need to check the existing structure for the Wind/Snow/Seismic loading dictated by today's IBC (IBC 2021 / ASCE7-16)?
This building was built in 2014. The state adopted IBC 2012 in 2014, thus this building could have been designed under IBC 2012 or IBC 2009. obviously we started using Vult for wind load calcs in ASCE 7-10. So if the building was designed using ASCE7-05, would the building need to be checked for ASCE 7-16 loading conditions?
Or are they saying that as long as they move the building within the same lot, you don't need to check the structure for today's code?
Furthermore, if I provide signed/sealed permit drawings for the relocation, I assume that I would take responsibility for the PEMB (not just the PEMB foundation). Thoughts?
IEBC CH 14 generally states, "Buildings shall comply with IBC provisions as applicable"
Does this mean that I need to check the existing structure for the Wind/Snow/Seismic loading dictated by today's IBC (IBC 2021 / ASCE7-16)?
This building was built in 2014. The state adopted IBC 2012 in 2014, thus this building could have been designed under IBC 2012 or IBC 2009. obviously we started using Vult for wind load calcs in ASCE 7-10. So if the building was designed using ASCE7-05, would the building need to be checked for ASCE 7-16 loading conditions?
Or are they saying that as long as they move the building within the same lot, you don't need to check the structure for today's code?
Furthermore, if I provide signed/sealed permit drawings for the relocation, I assume that I would take responsibility for the PEMB (not just the PEMB foundation). Thoughts?