I know this has been discussed a lot lately, see link below, but I am working on a project with a unique situation.
The building is a PEMB and they want to add solar panels to the roof which will weigh just under 3 psf. The building was constructed in 1996 under the BOCA code and was designed for a non-reducible roof live load of 30 psf. The building has since changed owners and the 30 psf is not a state or local requirement.
Per IEBC, the 3 psf exceeds the 5% rule so an analysis has to be done to confirm that it meets current codes (both wind uplift and the controlling downward cases). This building would be designed today for a 20 psf roof live load that is reducible. For the main frames, it would reduce down to 12 psf.
Is it reasonable to have a few sentences in the calcs explaining why the gravity load is okay based on the original design criteria but not actually run any numbers. I believe the roof snow load will be around 22 psf which is still less than the original 30 psf roof live load design even with the extra solar panel weight.
An analysis would still need to be done for the frames and purlins in uplift.
https://www.eng-tips.com/threads/ie...y-increase-on-total-load-or-load-type.529768/
I know this has been discussed a lot lately, see link below, but I am working on a project with a unique situation.
The building is a PEMB and they want to add solar panels to the roof which will weigh just under 3 psf. The building was constructed in 1996 under the BOCA code and was designed for a non-reducible roof live load of 30 psf. The building has since changed owners and the 30 psf is not a state or local requirement.
Per IEBC, the 3 psf exceeds the 5% rule so an analysis has to be done to confirm that it meets current codes (both wind uplift and the controlling downward cases). This building would be designed today for a 20 psf roof live load that is reducible. For the main frames, it would reduce down to 12 psf.
Is it reasonable to have a few sentences in the calcs explaining why the gravity load is okay based on the original design criteria but not actually run any numbers. I believe the roof snow load will be around 22 psf which is still less than the original 30 psf roof live load design even with the extra solar panel weight.
An analysis would still need to be done for the frames and purlins in uplift.