ahmedradi
Electrical
- Feb 2, 2009
- 5
Hi all,
I've got this software package that calculates the fault levels for our transmission network according to IEC60909 Method-C, which is the equivalent frequency method. Such as the make duty is calculated using instantaneous peak with DC component adjusted X/R is calculated at an equivalent frequency of 20Hz.
For a 50Hz system, such as our, the break duties (symmetrical and asymmetrical) are calculated based on the specified break time (this supposedly includes the breaker opening time plus arcing time). The break times (below in seconds) are translated to an equivalent frequency to adjust the X/R to accurately calculate the DC component as follows:
0.00s <= Tbk < 0.01s Freq = 20.00 Hz
0.01s <= Tbk < 0.02s Freq = 13.50 Hz
0.02s <= Tbk < 0.05s Freq = 7.50 Hz
0.05s <= Tbk < 0.10s Freq = 4.60 Hz
0.10s <= Tbk <= 0.25s Freq = 2.75 Hz
Q1. Are my equivalent frequencies above correct?
Q2. Are there any CB that you are aware of that is faster than 0.01sec or too slow to be beyond the 0.25sec?
Q3. This is the most important of all. According to the software package, I've ended up with a very puzzling break duties, which I couldn't explain from an engineering point of view or mathematically, and that is if I increase the break time, e.g. from 0.01 to 0.25, my break duties are increasing, as if slower breaker would need to be of higher interrupt capabilities!
To make matters worse, the break duties are even higher than make duties. I suspect that there is a bug in the software, but let me first hear from you based on your experience.
The data looks alright, yes there are some anomalies as in every utility, especially at generation sites, e.g. the transient and sub-transient reactances are of the same value, but further out at purely load substations, it is same problem!
Many thanks in advance for your inputs.
I've got this software package that calculates the fault levels for our transmission network according to IEC60909 Method-C, which is the equivalent frequency method. Such as the make duty is calculated using instantaneous peak with DC component adjusted X/R is calculated at an equivalent frequency of 20Hz.
For a 50Hz system, such as our, the break duties (symmetrical and asymmetrical) are calculated based on the specified break time (this supposedly includes the breaker opening time plus arcing time). The break times (below in seconds) are translated to an equivalent frequency to adjust the X/R to accurately calculate the DC component as follows:
0.00s <= Tbk < 0.01s Freq = 20.00 Hz
0.01s <= Tbk < 0.02s Freq = 13.50 Hz
0.02s <= Tbk < 0.05s Freq = 7.50 Hz
0.05s <= Tbk < 0.10s Freq = 4.60 Hz
0.10s <= Tbk <= 0.25s Freq = 2.75 Hz
Q1. Are my equivalent frequencies above correct?
Q2. Are there any CB that you are aware of that is faster than 0.01sec or too slow to be beyond the 0.25sec?
Q3. This is the most important of all. According to the software package, I've ended up with a very puzzling break duties, which I couldn't explain from an engineering point of view or mathematically, and that is if I increase the break time, e.g. from 0.01 to 0.25, my break duties are increasing, as if slower breaker would need to be of higher interrupt capabilities!
To make matters worse, the break duties are even higher than make duties. I suspect that there is a bug in the software, but let me first hear from you based on your experience.
The data looks alright, yes there are some anomalies as in every utility, especially at generation sites, e.g. the transient and sub-transient reactances are of the same value, but further out at purely load substations, it is same problem!
Many thanks in advance for your inputs.