Hi Folks
I have a situation where a wall (forming part of an intake tower on a dam project) has areas of very high shear as a result of massive hydrostatic pressures on the wall. The back of the wall is "propped" by slab sections at certain intervals, so the high shear occurs where the wall and slabs join. The wall is very thick (2.3m) but still localised shear stresses are as high as 3Mpa. Now according to British Design Codes this can be dealt with as long as it does not exceed 0.8*?fcu or 5MPa, whichever is less.
I attach a image from the analysis model where it can be seen where the high stresses occur. The openings are for pipes. It can be seen that the highest stresses are at the edges of the slabs at the back of the wall, which makes sense.
My question is, how would you reinforce this wall against shear? My thinking is to first calculate the wall shear resistance, vc, as per the formula in BS8110 using the reinforcement provided in the wall. Then to provide shear links as per the formulas given for slabs or beams and placing shear links in all areas where the shear stress exceeds vc.
What would you guys suggest? Please keep your suggestions simple if possible, I would like to find a basic way of dealing with the shear stresses. I am not used to deal with high shear in walls, usually shear comes into play in beams and punching shear on slabs, pads and pilecaps. It may therefore be beneficial to see the wall as a vertical slab and reinforce accordingly.
I have a situation where a wall (forming part of an intake tower on a dam project) has areas of very high shear as a result of massive hydrostatic pressures on the wall. The back of the wall is "propped" by slab sections at certain intervals, so the high shear occurs where the wall and slabs join. The wall is very thick (2.3m) but still localised shear stresses are as high as 3Mpa. Now according to British Design Codes this can be dealt with as long as it does not exceed 0.8*?fcu or 5MPa, whichever is less.
I attach a image from the analysis model where it can be seen where the high stresses occur. The openings are for pipes. It can be seen that the highest stresses are at the edges of the slabs at the back of the wall, which makes sense.
My question is, how would you reinforce this wall against shear? My thinking is to first calculate the wall shear resistance, vc, as per the formula in BS8110 using the reinforcement provided in the wall. Then to provide shear links as per the formulas given for slabs or beams and placing shear links in all areas where the shear stress exceeds vc.
What would you guys suggest? Please keep your suggestions simple if possible, I would like to find a basic way of dealing with the shear stresses. I am not used to deal with high shear in walls, usually shear comes into play in beams and punching shear on slabs, pads and pilecaps. It may therefore be beneficial to see the wall as a vertical slab and reinforce accordingly.