Lion06,
Thanks for the star. I never used to get any at school so this helps to make up for it.
RE Mxy, it is unfortunate that some people who are advising others how to design do not know what they are talking about!
The accuracy of the multiplier approach varies for different members depending on member shape, stress levels, concrete properties, loading patterns and a lot of other things. It cannot be quantified as 2 (A bit like the number 42!!!! representing 'the meaning of life, the universe, and everything'). It can vary from 1-1.5 to 6-9 depending on the situation.
Ishvaag,
You can keep your head in the sand as long a you like. I prefer to have a reasonable ball park guess as to my expected deflections, rather than not knowing which ball park I am actually in by using a multiplier method. And compared to test results in experimental studies and comparisons with buildings done by others, RAPT's answers are in the right ball park at least!
In a test at UNSW by Gilbert and others, reported in ACI several years ago, ACI expected deflection after 270 odd days was about 9mm. Actual was 29.1mm. RAPT was 30.5mm. I much prefer RAPT's answer to ACI code, even if it is over-estimating the deflections!!