Actually, the elevation really only has a role if the modification leaves the evaporator higher in the system than it is now. If you run the pipe up and then back down then the heights cancel each other out. What does have a significant effect is the new length of piping added: going up, going across, and coming down. That piece would be fairly significant as the friction head loss increases linearly with length of pipe, unless you go to a larger diameter pipe.
Remember Bernoulli's equation? (The total head loss = the change in elevation plus the change in system pressure head, plus the change in velocity head) where the change in the velocity head is a function of the friction factor times the pipe length times the velocity squared and divided by the pump diameter (with the gravity constant thrown in to keep units straight)
You can use the pump affinity laws to do a rough estimate of the effect, assuming you don't change pipe size. Specifically: for a given change in speed, the flow rate changes linearly, the head loss changes with the square root and the horse power changes with the cube root. If you hold speed constant, you can also define the change in head loss in terms of its effect on either pump horsepower or capacity.
Given the above, I did some rough calculations that assumed that the evaporator ended up on the same level as it was originally (i.e., that the relative elevation of the sump and evaporator to each other did not change). Working in whole numbers for simplicity, I took the current piping length as 6' up, 1' across, and 6' down for a total of 13'. For the new design, I used 12' up, 40' across, and 12' down for a total of 64'. Thus the length increased by a multiple of 5. Since the head loss is proportional to the length, I assumed the head loss would also increase by 5. If I assume that the pump speed can vary, but that capacity and hp are fixed, then the speed would need to increase by the square root of 5 or by 2.2. If I assume that the capacity and pump speed are fixed, then the hp needed would increase by 11 (51.5). Based on these rough estimates, I doubt your pump will handle the change, unless you go to a bigger pipe diameter.
Using the Bernoulli equation and the affinity laws, you could work this out on paper before you make any physical changes.