I used to work for a fan manufacturer and the curves described are quite normal. Most manufacturers publish the stable part of the curves and 'grey out' the less useful part. However this doesn't mean you cant use it, its just unstable,
Let me explain, at unstable points on the curve, the flow can become pulsing and cause vibration etc. but the fluid is still moves. also at some point on the curve, there can be 2 operating points and the pump/fan will hunt between curve points.
If the fan is used for emergency purposes, i.e. for only intermitent or one off conditions like fire extract, then its not really a problem since the fan is a one off use anyway.
Operating something long tern obviously isn't recommended.
There are pro's and con's for publishibg the whole curve. If you grey out the curve, then the user is not tempted to use the greyed out section. (But some people assume that the curve simply carries on up. (Fatal mistake).
If the manufacturers shows the whole curve, there is the risk that the eselctor can try and use the curve at an inappropriate condition.
Try to use the curve no more than 65-75% from the base to keep well in and create stable operating conditions. People quite often clip the underside of the curve and get away with it, but its not worth the risk.