we have a vessel to protect by overpressure during a fire, the fluid has a critical pressure below the set pressure of the PSV so there isn't true latent heat.
How must the flowrate of fire contingency be set?

Tx for replies
 
Treat this vessel as if it is gas filled, because in a sense, it is. You need to protect it by means that either don't reseal (rupture disk or buckle pin etc), or thermally.
 

It's important to understand that safety valves are generally incapable of protecting a vessel from fire exposure unless that vessel is at least partly filled with liquid, and that liquid will boil at a temperature that is not too excessive.

Moltenmetal provided real good advice - treat this supercritical fluid as if it's a gas - a very high density gas. If you're going to rely entirely on a relief device to protect a gas filled vessel from fire, then a non-reclosing device is what you need. A safety valve will not prevent the vessel from failing.

I just wanted to add that there's an alternate solution, if you hate rupture disks as much as I do. Whenever you use disks, you have to worry about premature disk failure, and that in itself can have some pretty unacceptable consequences. The alternative is to use a safety valve, but rely on other means to provide real protection. That is, use one, or any combination of the following protective measures, depending on the severity of the hazard: (1) auto depressurization, (2) water spray, (3) fire resistant insulation.
 
...or a fusible plug, which is what I meant by "thermally".
 
Ryan Ouderkirk published a paper "Rigorously Size Relief Valves for Supercritical Fluids" in CEP August 2002 that may provided a method for this case.
 