It's important to understand that safety valves are generally incapable of protecting a vessel from fire exposure unless that vessel is at least partly filled with liquid, and that liquid will boil at a temperature that is not too excessive.
Moltenmetal provided real good advice - treat this supercritical fluid as if it's a gas - a very high density gas. If you're going to rely entirely on a relief device to protect a gas filled vessel from fire, then a non-reclosing device is what you need. A safety valve will not prevent the vessel from failing.
I just wanted to add that there's an alternate solution, if you hate rupture disks as much as I do. Whenever you use disks, you have to worry about premature disk failure, and that in itself can have some pretty unacceptable consequences. The alternative is to use a safety valve, but rely on other means to provide real protection. That is, use one, or any combination of the following protective measures, depending on the severity of the hazard: (1) auto depressurization, (2) water spray, (3) fire resistant insulation.