Sawsan311 said:
I would like to enquire about the restricted lift option, can this be considered a temporary solution for any chattering situation?
Implementing restricted lift (RL)
may solve a chattering problem, but whether it does or not will depend on the reason for the chattering in the first place. There are multiple causes of chatter, and without experimental testing of the installation, one can never be certain which potential cause is the true cause.
Implementing RL is beneficial in reducing the risk of chatter because it increases the net lifting force on the PSV. It does that by reducing the pressure loss in the pipe, thus creating a greater dP across the PSV itself. So, yes, it's a reasonable/acceptable modification for an existing PSV that's known to chatter, or for a new installation that has excessive piping pressure losses. Effectively, RL reduces the orifice area of the PSV, thus resulting in a lower
rated capacity for that valve. Since pressure loss increases square to the flow, a small reduction in rated flow results in a relatively large reduction in pressure loss.
If the chattering is caused by acoustic phenomena then, of course, implementing RL may not solve the problem. Refer to API 520 Pt II for: (1) the latest knowledge about what causes of chatter, (2) an explanation on how to assess the risk of chatter, and (3) design measures which can reduce that risk.
And, BTW, there's no reason to regard RL as a "temporary" fix. When used, it's generally done as a "permanent" part of the relief design. If one wants to reverse an RL modification, that's easy to do. Just send the PSV to the valve shop and have the RL (mechanical stop) removed.