KarlT
Structural
- Feb 6, 2003
- 120
I am working on a project (in Canada where it's cold and snowing!) in which we are removing the existing brick veneer in a concrete block cavity wall, applying a new air/vapour barrier, new brick ties, insulation and installing a new brick veneer wythe.
The structural wythe is an existing 12" block wall, with a clear span of 22'6" from the bottom of the wall to the underside of some existing 42" deep joists. The bottom of the joists are tied to the block wall with weld plates, and the diagonal bridging is tied to the non-load bearing block walls with plates at the underside of joist elevation.
We are using newer rigid "l-ties", which will be fastened to the existing block with 2 epoxy set inserts, allowing the wall to act partially composite with the brick. The problem is that even accounting for the benefits of partial composite action, the allowable tensile stresses in the existing block are exceeded implying that I now need to reinforce the wall.
The stupid thing is that this wall has been in service since 1977 and has been performing fine since then. The wall was well constructed (based on site observations)and there are no visible signs of any cracking or distress. There are many examples of walls like this one that are all performing well, but they do not meet the newest codes. Is it typically assumed that once you touch the wall, you need to bring it up to codes, or can you say since it has been performing well we can leave it alone?
By the way, I am strongly leaning towards grouting in bars to satisy the code because in the grand scheme of things it's cheap insurance to do what I assume is required.
How does everyone else deal with type of problem?
The structural wythe is an existing 12" block wall, with a clear span of 22'6" from the bottom of the wall to the underside of some existing 42" deep joists. The bottom of the joists are tied to the block wall with weld plates, and the diagonal bridging is tied to the non-load bearing block walls with plates at the underside of joist elevation.
We are using newer rigid "l-ties", which will be fastened to the existing block with 2 epoxy set inserts, allowing the wall to act partially composite with the brick. The problem is that even accounting for the benefits of partial composite action, the allowable tensile stresses in the existing block are exceeded implying that I now need to reinforce the wall.
The stupid thing is that this wall has been in service since 1977 and has been performing fine since then. The wall was well constructed (based on site observations)and there are no visible signs of any cracking or distress. There are many examples of walls like this one that are all performing well, but they do not meet the newest codes. Is it typically assumed that once you touch the wall, you need to bring it up to codes, or can you say since it has been performing well we can leave it alone?
By the way, I am strongly leaning towards grouting in bars to satisy the code because in the grand scheme of things it's cheap insurance to do what I assume is required.
How does everyone else deal with type of problem?