Hi all, I need to make a 3phase rotation meter (to measure rotation for 400V,50hz,incoming supply from diesel) since we don't have one (we will get one soon). The test equipments which we suppost to receive are missing and its a long story. To check and confirm the incoming phase rotation is a requirement for the client.
I have 1 capacitor 3uF (+-5%)/400Vac/40-60-Hz, 2 bulbs (filamen type)220volt, 50w. All these are cnnected in star with capacitor in L3, bulb no.2 in L2 and bulb no.1 in L1.
First question, what is the capative reactance at 50Hz, since the power frequency available is 50Hz? I am confused with the rating 40-60hz.
Say the cap. is same 3uF,so the -jXc is 1/(2*pi*50*3uF) = 1.06kohm. Each bulp is 220v*220v/50w = 0.968kohm.
Second question, the cap. reactance and bulp ohmic value are bit different is this acceptable?
3rd question, two bulps will have 400v accross their terminal and this should be allrite, correct?
4th question, Neutral Voltage formula is =Ya*Van+Yb*Vbn+Yc*Vcn/Ya+Yb+Yc
Guys I need your input before I make one. I shall draw and attach a file in the next post.
Thanks in advance.
I have 1 capacitor 3uF (+-5%)/400Vac/40-60-Hz, 2 bulbs (filamen type)220volt, 50w. All these are cnnected in star with capacitor in L3, bulb no.2 in L2 and bulb no.1 in L1.
First question, what is the capative reactance at 50Hz, since the power frequency available is 50Hz? I am confused with the rating 40-60hz.
Say the cap. is same 3uF,so the -jXc is 1/(2*pi*50*3uF) = 1.06kohm. Each bulp is 220v*220v/50w = 0.968kohm.
Second question, the cap. reactance and bulp ohmic value are bit different is this acceptable?
3rd question, two bulps will have 400v accross their terminal and this should be allrite, correct?
4th question, Neutral Voltage formula is =Ya*Van+Yb*Vbn+Yc*Vcn/Ya+Yb+Yc
Guys I need your input before I make one. I shall draw and attach a file in the next post.
Thanks in advance.