is it possible for me to power a 10HP three phase induction motor from a single phase (60A) domestic supply? how so?
 
Replies continue below

Recommended for you

It depends on what voltage you have available.

At 110 or similar voltages, it won't be possible since 110*60=6600 W, which is short of the cirka 7500 W needed by the motor even before you start looking at efficiency and power factor.

At 220 - 240 V, it could work. Especially if you van find a frequency inverter (VFD) of suitable size. Or a rotary converter. Starting the machine could be a problem, though.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 