davva
Marine/Ocean
- Sep 27, 2004
- 99
I took these waveform measurements of an open transition autotranformer, 65% tap, motor starter (1700kW rating).
The generation system is a ships network with two 2.4MW 440V generators.
The two waveforms are the start and the run circuit breakers closing. Run closes 40secs after start and the motor is fully up to speed after 16 secs and remains unloaded.
There is a very severe voltage drop when the run contactor closes.
I am aware that open transition motor starters shouldn't be used in weak generation networks. But this system has been in place for 7 years and they are only noticing problems recently with some newly installed downstream equipment falling over as it can't handle the drop.
I made severly repeat starts and the voltage drop on RUN changeover was much less (410V).
I made the assumption that the inherent starter design is at fault with the system that it is installed in. However, I don't understand what is happening in the circled area where the voltage flattens out then drops further. Could this be an intermittent AVR problem or the poor contacts/contact bounce of the circuit breaker?
Appreciate any help/comments.
The generation system is a ships network with two 2.4MW 440V generators.
The two waveforms are the start and the run circuit breakers closing. Run closes 40secs after start and the motor is fully up to speed after 16 secs and remains unloaded.
There is a very severe voltage drop when the run contactor closes.
I am aware that open transition motor starters shouldn't be used in weak generation networks. But this system has been in place for 7 years and they are only noticing problems recently with some newly installed downstream equipment falling over as it can't handle the drop.
I made severly repeat starts and the voltage drop on RUN changeover was much less (410V).
I made the assumption that the inherent starter design is at fault with the system that it is installed in. However, I don't understand what is happening in the circled area where the voltage flattens out then drops further. Could this be an intermittent AVR problem or the poor contacts/contact bounce of the circuit breaker?
Appreciate any help/comments.