Comment on ScottyUK (Electrical) Mar 3, 2004 marked ///\\A basic principle of any transformer is ampere-turn balance. Thus, primary amps x primary turns = secondary amps x secondary turns.
///Agree\\By opening the secondary with the primary energised, you are upsetting the ampere-turn balance relationship.
///Not true. See Reference:
Gordon R. Slemon "Magnetoelectric Devices Transducers, Transformers, and Machines," John Wiley & Sons, Inc., 1966,
page 201, Figure 3.17 a) Current Transformer and b) Equivalent Circuit,
where the ampere-turn balance still exists; however, it is changed due to the burden circuit branch being open.
Clearly, Fig. 3.17 b) indicates a current I1'=N1xI1/N2 flowing through the CT transformer secondary winding to the point where it branches to the CT burden branch and to the CT magnetization branch with magnetization admittance Y1m. If the burden circuit is open, then the current I1'=N1xI1/N2 flows through Y1m only causing the high voltage on the CT secondary dependent on complex number value of Y1m.\\ In order to maintain ampere-turn balance, the secondary voltage rises until insulation breaks down allowing current to flow and restore balance,
///Why would the insulation break down if it happens to be rated higher than the secondary CT open circuited voltage?\\ or until the core saturates.
///Yes, the core usually saturates with high voltage across the Y1m branch due current I1' being high through Y1m.\\ Saturation of the iron core keeps the voltage well below its theoretical limit,
///Please, clarify the "theoretical limit."\\ although a big CT will easily develop several kV open circuit, more than enough to kill you.
///Yes, certainly it could.\\\