I have heard of limitations for synching across breakers, since having the sides 180 degrees out of phase puts 2x stress on the open contacts. Sorry I don't have a specific reference for that.
Hey Bacon, I don't have a reference for that either, but I know in Ontario's post-2003-blackout reviews the system design and operating people were horrified to find out that there were locations in the province where islands had been synchronized with breakers that weren't rated for 180° out of phase voltage. I don't recall there being any reports of breaker damage found post-event, but there definitely was discussion around replacing specific breakers with ones having said 2x rating along system restoration paths.
bacon4life:
In my state the rules for clearances require a visual open, which in some cases gives a slight preference for normal open points to be air break disconnects rather than SF6 breakers.
Hmmm, visual open points . . . I don't know of any breaker the contacts of which can be visually verified open, but the SF
6 disconnects in series with them for maintenance/isolation purposes most commonly have sight ports for this, and my utility routinely used these switches as visually verifiable open points for work protection purposes.
One non-utility generation site encountered a billing metering issue that caused them to choose to run with their SF
6 ring bus open [using breakers] between their two outgoing circuits until their units were generating > 100 MW; no impediments were found to constrain this practice.
There was a vintage of SF
6 breaker-and-a-half switchgear that had problems where the voltage measuring equipment could burn up if a line terminal's disconnect and breakers were left open due to the terminal bus having voltage applied to it via the breaker's grading capacitors; special operating procedures were developed to mitigate the risk of this.
All that being said, there may be other constraints out there that I never encountered . . .