Neplan: PHASE and LINE Voltage
FedericoZ
4
Hello every one. I am an electrical engineer, and a newbie using Neplan.
I made a little Network and want to calculate the LOAD FLOW.
When I calculate the LOAD FLOW there is no error, but viewing the results Neplan shows me the PHASE Voltage, instead of LINE Voltage. How can I tell it to show me the Line Voltage?
Thanks in advance for the help.
Federico
Ciao Federico,
which version of Neplan do you use?
I use Neplan ver. 5.2.0. It's a Demo version.
Please note that now the 5.2.3 ver is available.
To select the results to show on the screen, double click on an empty zone of the circuit window. A mask will appear. Then choose the Load Flow tab and select all the results you want to see. Click OK and ... et voila'!
Maybe I did not explain myself.The problem is not to see the results, but the way the results are shown.
I want to see The LINE voltage (Tensione concatenata) but Neplan shows me the Phase voltage (Tensione di fase x ogni fase).
I followed your suggestion but nothing happened.
I re-drawed the network in a new sheet and now it shows the results in the way I want to see. Why? How can I toggle from the various way to view the results?
Thanks for your answers.
Federico
I confirm you that Neplan shows the phase-to-phase voltage. I remember that there were some problems with the angles of voltages and currents. But I sent a note to the authors of the prg.
Anyway the "rated voltage" described in the manual is what you are looking for.
If you still have problem, please contact your local consultant of BCP!