Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JAE on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Need help with foundation pressure diagram

Status
Not open for further replies.

Buleeek

Structural
Joined
Sep 5, 2017
Messages
98
Location
PL
Hello,
Can someone help me with a pressure diagram to the attached situation? Load "A" is symmetrical and concrete load can be omitted. I think I know what the q.max is, but where exactly does the pressure reach zero ?

Thanks in advance.
 
 https://files.engineering.com/getfile.aspx?folder=486fbe95-f85c-4ac0-bba4-1fe8c354f192&file=IMG_0776.JPG
The pressure doesn't reach zero. If you consider deflection of the foundation, pressure will not be exactly uniform, but will depend on the stiffness of the concrete and the properties of the soil. The diagram in orange below shows the soil pressure for a stiff foundation.

image_qd9gzk.png


BA
 
Assuming A=A (i.e. those point loads are equal).....the pressure underneath will be uniform. That is (of course) a design assumption good enough for calculations. In reality the pressure will be (locally) higher under the point loads the stiffer the soil is.

 
And if you can increase the 1' distance to 2'...

Rather than think climate change and the corona virus as science, think of it as the wrath of God. Feel any better?

-Dik
 
BA,
Where can I get more information about that foundation stiffness? Also, What would the diagram be if the load was not symmetrical (for instance only one force A instead of two) ?
Thanks,
 
Foundation stiffness is EI where E is Young's modulus and I is the moment of inertia. You will also need properties of the soil. Deflection is dependent on both of those. A beam on an elastic foundation is a fairly advanced type of calculation. I suggest you assume the beam to have infinite stiffness or, in other words, that it acts as a rigid body. Or in still other words, the soil pressure will be assumed to be linear.

If the load is not symmetrical, find the c.g. of load. If it lies within the kern of the foundation, use the formula given by Celt83 above.

If the c.g. of load 'P' is outside the kern of the foundation, there will be a point where the pressure equals zero. That will occur at a distance 'D' from the end nearest the c.g. The maximum pressure will be at the end and will have magnitude of twice the average pressure, or 2*P/B*D.

Effective length D = 3*C where C is the distance between the end of foundation and the c.g. of load.

For your foundation, the kern of the section is the middle third of the 10' length. If the eccentricity is less than 10/6 = 1.667', it is within the kern, so:
Pressure 'q' = P/A +- P*e/S where A is area of contact and S is section modulus.

If e > 1.667, then the effective length of footing is 3*C;
so qmax = 2*P/3*C and qmin = 0.
Beyond the effective length, the footing rises off the ground and pressure is zero.
 
BA,

Thank you for the explanation.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top