Aug 10, 2020 #1 cdafd Specifier/Regulator Joined Aug 18, 2005 Messages 2,953 Location US Pendent Regular pendent sprinkler/ non moving deflector Installed with drop in ceiling. How far below drop ceiling does the deflector have to be?? I thinking install per manufacture? NFPA 13 sections would help if any
Pendent Regular pendent sprinkler/ non moving deflector Installed with drop in ceiling. How far below drop ceiling does the deflector have to be?? I thinking install per manufacture? NFPA 13 sections would help if any
Aug 10, 2020 1 #2 MGXFP Mechanical Joined Jul 30, 2002 Messages 426 Location US For unobstructed construction pendent deflectors must be 1-12" below finished ceilings unless listed otherwise. Some are listed to be a fraction of an inch below finished ceiling. 10.2.6.1. Upvote 0 Downvote
For unobstructed construction pendent deflectors must be 1-12" below finished ceilings unless listed otherwise. Some are listed to be a fraction of an inch below finished ceiling. 10.2.6.1.
Aug 10, 2020 Thread starter #3 cdafd Specifier/Regulator Joined Aug 18, 2005 Messages 2,953 Location US Thanks, Not sure why the question has not come up before, in my mind. Just happen to be at a retro drop ceiling install, and the question came up. Upvote 0 Downvote
Thanks, Not sure why the question has not come up before, in my mind. Just happen to be at a retro drop ceiling install, and the question came up.
Aug 11, 2020 #4 SprinklerDesigner2 Mechanical Joined Nov 30, 2006 Messages 1,281 Location US I agree 1 to 12 inches unless listing says otherwise. Upvote 0 Downvote
Aug 11, 2020 Thread starter #5 cdafd Specifier/Regulator Joined Aug 18, 2005 Messages 2,953 Location US Update For this job it is using about 25 year old Reliable Rasco G1 concealed sprinkler. Deflector does not move. Reliable said if the concealed cover goes on,,, the sprinkler deflector is in the proper position. Upvote 0 Downvote
Update For this job it is using about 25 year old Reliable Rasco G1 concealed sprinkler. Deflector does not move. Reliable said if the concealed cover goes on,,, the sprinkler deflector is in the proper position.