I have a question about the installation of the beam detector.

Status
Not open for further replies.

Mike Hou

Industrial
Joined
Oct 26, 2024
Messages
3
Is it correct to install a beam detector on this site? Is there a NFPA regulation on this?圖片_20241026133551.jpg
 

Attachments

  • 圖片_20241026133607.jpg
    圖片_20241026133607.jpg
    196.3 KB · Views: 4
As long as installed per manufacture instructions,,,, I see no problem

Normally I see them lower on the wall
 
Why the question
 
Why the question
because about Factory inspection team request we install location likt picture, but The instruction manual requires that the beam detector should be 1 meter above, below, left, and right side without any obstructions............
 
I would call manufacture tech support

Ask them if it is ok.
 
NFPA 72 Fire Alarm Code - see attached excerpt, assuming this is a beam type smoke detector.
 

Attachments

  • Screen Shot 2024-11-07 at 6.04.31 PM.png
    Screen Shot 2024-11-07 at 6.04.31 PM.png
    244.7 KB · Views: 6