Depending on the block producer, the number you mentioned may meet the "cook-book" code standards. If a higher f'm is required, it can be met easily. There have been some tests done that will eventually change the relationship between the unit strength and prism strength, but the gears move very slowly when it comes to codes and standards. An actual prism test "trumps" everything, even with conservative codes.
I have made 8" hollow prisms that tested 4800 psi with 2500 psi mortar using 8500 psi unit strength hollow block. I could never find an engineer that could find an excuse to use the combination that provided the strength.
Unfortunately, the ASTM specs for block are so low no producers bother to test for compressive strength because the present manufacturing processes, there is no cost advantage to make the old low strength, because the cost of a minimal block is higher. There is nothing wrong to specify a higher f'm if it can be documented.
If it is just a minimal,routine use, just stick to the older concepts, but if you need high strength, it can be obtained easily. Others use our codes and standards, but others build 20 story partially reinforced loadbearing masonry by using the same codes, but by using them better. - Very few clean-outs and all products color coded for strength and approved before delivery.
Dick