I personally reinforce full depth, but I'm aware of some people who only provide reinforcing for bending through the upper portion of the pile with the reasoning that below a certain point the moment becomes negligable. This probably makes some sense if you're working with extremely long piles.
Anyway, pile geotech design is mostly done by computer now, so the moment diagram isn't any harder to provde than a max value.
The standard column load interaction diagrams aren't going to be that useful. They'll all just tell you to use minimum steel, generally while showing that you're only using a few percent of the moment capacity. You may have to build your own interaction diagrams or otherwise design the members to avoid having a ridiculous amount of reinforceent.
Also, be aware that there may be separate code requirements for piles. For instance, in the Canadian code you have to ignore the outer inch of concrete for uncased ples and then reduce the capacity of the member by an additional factor of 0.9. There are also requirements for pile reinforcement in seismic areas to ensure ductility.