lexatus-
This is not an error. We design buildings with "wind clip" connections every day. I didn't chime in earlier because you said the FRAMES looked light. In actuality a "wind clip" building will have heavier beams and lighter columns, not lighter members all around. The reason for this is that while the connections only take wind load, you assume a pin-pin design for the beam for gravity. That is obviously the worst case for gravity and will result in a heavier beam than assuming the beam is fixed at the columns. It also lightens up the columns because there is less moment getting thrown into the columns (wind load only, not wind plus gravity). It is covered quite well in Blodgett's book, but he really only touches on top plates with a bottom angle. We typically design them with top and bottom angles. Lou Geschwindner has several good papers on this topic (including one that I posted a long time ago involving the frame stability under these conditions.
While it is true that the moment in the connections won't always be due to the wind load effect, if designed properly it will never have more moment in it than the wind load moment (they're typically never right on the money, so you'll get some nominal amount over the wind moment).
Quick synopsis............ The connections are designed for wind load only. The beam is loaded with gravity and both connections yield at the wind load moment. The wind blows and the leeward connection tries to load further, but it can't because it's already yielded, so the total wind load moment gets thrown into the windward connection which can now absorb twice the wind load moment because it is trying to unload so it accepts "its own" wind moment to unload back to 0, then accepts "the leeward connection's" wind moment to get to the absolute value of the wind moment with the opposite sign.
That's the worst case. You can have the situation where the connections don't yield under gravity loads and some of the leeward connection does see some amount of wind moment before it yields and starts dumping additional moment into the windward connection. That is less common and not worth the time to look at (typically in our office, anyway).
As I said, though, that only makes the columns and connections lighter, but it actually makes the beams heavier.