I currently have a Joist header (2 ply 2x8 SPF) that spans 10ft that supports 9 joists (2x8) with 5 being 70in long and 4 being 84in long. No joist hangers on the joist to header connection just 3 nails from the back of the header into the joist.
The previous owners of the house had done some modifications in the basement and I'm only guessing there might have been a load bearing wall beneath the joist header so approximately 2in away from the joist header a beam was placed below it (3 ply 2x8 with a 2x4 top plate).
I would like to remove this beam as it cuts into my headroom in my basement. I have measured the deflection of the beam using wire attached to either end of the beam and measured multiple points to determine the low spot. The deflection I measured was 5/32" which using a uniform load assumption gives a loading of about 205plf which is close to my estimate of 220plf.
I don't want to remove the existing joist header so to carry the load and minimize deflection I intend to add 2 more 2x8s SPF gr. 2 and through bolt this modified joist header (now it would be 4 ply 2x8) with 1/2" bolts, qty: 2 spaced 16in apart. And after I remove the lower beam reinforce the joist connections with joist hangers (manufacturer: USP JUS28).
The only thing I'm having a hard time finding any information on is regarding side loaded beams. The joist hanger manufacturers have some derating tables but are there any design guidance regarding one side loaded flush beams or joist headers? I'm not sure if I will have a load path issue with 4ply 2x8 beam if only one face is loaded.
The previous owners of the house had done some modifications in the basement and I'm only guessing there might have been a load bearing wall beneath the joist header so approximately 2in away from the joist header a beam was placed below it (3 ply 2x8 with a 2x4 top plate).
I would like to remove this beam as it cuts into my headroom in my basement. I have measured the deflection of the beam using wire attached to either end of the beam and measured multiple points to determine the low spot. The deflection I measured was 5/32" which using a uniform load assumption gives a loading of about 205plf which is close to my estimate of 220plf.
I don't want to remove the existing joist header so to carry the load and minimize deflection I intend to add 2 more 2x8s SPF gr. 2 and through bolt this modified joist header (now it would be 4 ply 2x8) with 1/2" bolts, qty: 2 spaced 16in apart. And after I remove the lower beam reinforce the joist connections with joist hangers (manufacturer: USP JUS28).
The only thing I'm having a hard time finding any information on is regarding side loaded beams. The joist hanger manufacturers have some derating tables but are there any design guidance regarding one side loaded flush beams or joist headers? I'm not sure if I will have a load path issue with 4ply 2x8 beam if only one face is loaded.