Sep 17, 2002 #1 anna8 Electrical Joined Sep 17, 2002 Messages 4 Location GB Where can I obtain detailed modelling data for fault and dynamic analysis for AC 1MW -5MW generators?
Where can I obtain detailed modelling data for fault and dynamic analysis for AC 1MW -5MW generators?
Sep 18, 2002 #2 incline45 Electrical Joined Aug 21, 2002 Messages 2 Location CA Manuf should provide. I have some generator dynamics for 5MW mach but no gov. Upvote 0 Downvote
Sep 20, 2002 #3 cuky2000 Electrical Joined Aug 18, 2001 Messages 2,135 Location DO Here are some typical mean values: Reactances Type of Gen Subtransient Transient Steady-State Turbogenerator 10-20% 15-25% 150-230% Salient-pole gen. 15-25% 25-35% 70-120% See the enclose document with typical sequence resistance and reactance for small generator http://www.powerstudies.com/content/resources/LOWZERO.pdf The enclose have some additional information that could be use thread237-27981 Good luck. Upvote 0 Downvote
Here are some typical mean values: Reactances Type of Gen Subtransient Transient Steady-State Turbogenerator 10-20% 15-25% 150-230% Salient-pole gen. 15-25% 25-35% 70-120% See the enclose document with typical sequence resistance and reactance for small generator http://www.powerstudies.com/content/resources/LOWZERO.pdf The enclose have some additional information that could be use thread237-27981 Good luck.