In modelling techniques for power system analysis. Considering the ONAN and ONAF ratings for a transformer; which rating should be considered as the Base MVA for p.u unitization?
The transformer nameplate should tell you. Most I’ve seen use the self cooled ONAN value, but I’ve come across a couple at my company that use the force cooled maximum ONAF values.
The maximum rating is used in the IEC world as the pu base; the self-cooled rating is used in the IEEE world. In IEEE World impedance etc are also expressed on ONAN base,