Hi,
The HI standard 9.8 "Intake Design for Rotodynamic Pumps" states that the Minimum Submergence for a horizontal bottom outlet from a tank can be given by S=D (1+2.3Fr) where D is the nozzle diameter and Fr is the Froude number
The Froude No. Fr = V / SQRT(g*D)
where
V = nozzle velocity
g = gravity constant.
My query is for a rectangular outlet nozzle, should I use an equivalent hydraulic diameter for D such as
dh = 2 a b / (a + b)
where
dh = hydraulic diameter
a = width of the duct (mm, in)
b = height of the duct (mm, in)
or do I just use the height ‘b’ of the rectangular nozzle as the value for D?