Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

minimum air clearance in transmission line

Status
Not open for further replies.

samundra24

Electrical
Joined
Jun 11, 2011
Messages
15
Location
NP
I have this double circuit 220kV line and the formula used for designing minimum air clearance between conductor and earthed part is a = 6.5 inch per 10kV rms; Is this an european or US standard? Thanks in advance
 
Samundra24,
the clearance depends on the required impulse withstand (switching / lightening) and not on the nominal voltage, which generally dictates the creepage distsnce.
The correlation between standard rated voltages, rated impulse withstand voltages and minimum air clearances are reported in IEC 60071.
For a 220 kV system (Um=245 kV), the highest standard BIL is 1050 kV, leading to a standard conductor-structure clearance distance of 1.9 m.


Si duri puer ingeni videtur,
preconem facias vel architectum.
 
That doesn't sound like anything directly out of the USA NESC. Table 235-6 requires 11 inches + 0.2 inches per kV over 50 kV for the distance from conductors to the supporting structure.

Clearances from other objects such as buildings are typically listed as a base value plus 0.4 inches per kV over 22 kV phase to ground (6.92in/10 kV Phase to phase).
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top