the clearance depends on the required impulse withstand (switching / lightening) and not on the nominal voltage, which generally dictates the creepage distsnce.
The correlation between standard rated voltages, rated impulse withstand voltages and minimum air clearances are reported in IEC 60071.
For a 220 kV system (Um=245 kV), the highest standard BIL is 1050 kV, leading to a standard conductor-structure clearance distance of 1.9 m.