Metal Stud Flange Bearing

Status
Not open for further replies.

otto_eng

Civil/Environmental
Joined
Jun 27, 2017
Messages
88
Location
DE
Hi,

I am designing a metal stud wall for lateral and gravity. I'm planning to connect a metal track to flanges of the studs in order to carry the ceiling joists. I can not let them sit directly on the studs.
I was wondering if that would be an adequate design or not since 20 GA metal stud is not really thick. The shear on the connections is only 150 lb D+L.

Thank you,
 
The detail that you describe is typical. The roof joists usually sit on the top track. The joists should be checked for web crippling.

Attached is a guide with typically light gauge details.
 
 http://files.engineering.com/getfile.aspx?folder=241895bf-30d1-4045-8de5-0c6c71c9a14f&file=Low-Rise_Residential_Construction_Details.pdf
Hi ash060,

Thanks for your response but the wall is sticking in so I can not let them sit on the top track.
I need to attach roof joists to the metal track (ledger ) and the metal track ( ledger ) to the studs.
 
You need to know a little more than what you have stated. How are the wall studs braced? Dry-wall or bridging? In-plane or out-of-plane? Start with Cold Formed Steel Engineers Institute CFSEI
 
Provide a continuous cee ledger along the face of the studs and screw to the face of the wall studs. Just provide enough screws for the applied load.
 