I have a project to install solar panels on the roof of an existing municipal swimming pool building. The as-built drawings of the pool indicate that the dead load used for design of the roof OWSJ's was 20 psf.
Based on the construction of the roof system, I come up with a dead load of 12.3 psf for the roof construction. This means the EOR used an MEP allowance of about 7 psf.
This seems to be a bit too much for this building. There is ductwork, electrical (lights), and fire sprinkler system hanging from the joists. There is no ceiling (open to roof deck).
If this were an office building, I would typically use 10 psf for MEP. However, there is very little hanging from the roof, so I am inclined to use something around 3 to 5 psf for MEP.
I searched high and low for some kind of guidelines for MEP allowance but found nothing, other than references to 10 psf for office buildings. Anyone have rules of thumb that they use?