Oct 6, 2014 #1 mechfabricator Mechanical Joined Sep 28, 2014 Messages 10 Location AE what is the maximum inlet size for atmospheric tank as per api 650. can we put a 20" inlet nozzle in roof of tank?
what is the maximum inlet size for atmospheric tank as per api 650. can we put a 20" inlet nozzle in roof of tank?
Oct 7, 2014 #2 fegenbush Mechanical Joined Apr 5, 2006 Messages 783 Location US API 650 does not prescribe a maximum inlet size, but the maximum size listed in Table 5.6b is 60" NPS. Upvote 0 Downvote
API 650 does not prescribe a maximum inlet size, but the maximum size listed in Table 5.6b is 60" NPS.
Oct 7, 2014 #3 Duwe6 Industrial Joined Jul 27, 2010 Messages 2,189 Location US And please bear in mind that a generic roof design from 650 is essentially a 'rain hat'. It has no provisions for major loads, so it is incumbent on the tank designer to 'beef things up' to take that large, localized load. Upvote 0 Downvote
And please bear in mind that a generic roof design from 650 is essentially a 'rain hat'. It has no provisions for major loads, so it is incumbent on the tank designer to 'beef things up' to take that large, localized load.
Oct 7, 2014 #4 IFRs Petroleum Joined Nov 22, 2002 Messages 4,680 Location US Spash fill is not recommended for volatile products And what Duwe6 said. Upvote 0 Downvote