Years ago I cast some 3 meter thick X 5 meter wide compressor foundations in the Middle East. We waited till winter to do this and actually shot ourseleves in the foot because the night time temperatures created a differential that cracked the foundations. I have since been informed that the main objective here is to keep the temperature differential between the internal concrete and the exterior surface below 20 degrees C. To accomplish that you can start with chilled water and crushed ice in the mix, but I would also advise using a mix with some fly ash or blast furnace slag (GGBS) to slow down the curing rate and reduce the heat of hydration. We tracked the internal temperatures with thermocouples which reached 60 or 65 degress C as I recall, so you might actually have to provide some insulation around the foundations if your night time temperatures are falling near the 20 degree differential. I am not familiar with ACI 207 but companies that manufacture slag or fly ash should be able to provide helpful info on controlling the heat of hydration. If controlling the cracking is extremely critical (as it was with our compressor foundations) you might also consider casting a small mock-up and monitoring the interior and exterior tempratures.
Hope this info was helpful