rfisenne
Civil/Environmental
- Jun 12, 2002
- 1
I am reviewing plans for a new generator building and am a little concerned about the stability of the structure. The building is 40' x 24' by 10' high and built of concrete block. It has a scissor truss roofing system. The 24 foot walls are made up entirely of louvers for air intake so there is only a minimal (a 16" block return) to resist racking due to wind load on the 40' wall. There is no pilasters along the 40 foot wall and no steel moment frame to resist racking of the building. Anybody have any input about this? Other relevent info about the building..... IBC wind zone of 110mph. Block walls are reinforced with durowall every other course and has a horizontal reinforced bond beam every 4'. Do I need any more structural elements to resist racking in the 24' louver wall? Also cross bracing the 24' wall will not work due to the intake/exhaust ductwork for the generator.