Hi, I'm looking for a little more guidance on calculating the neutral axis for a masonry wall when the neutral axis is not within the face shell thickness. I worked through one scenario below, but the result obviously looks wrong. The formula to calculate k looks wrong under further scrutiny, doesn't look like a positive value would result in any case?
I assumed the following:
(1) Allowable stress design
(2) 8" thick wall
(3) Partially grouted with 1-#5 at 24" spacing
From NCMA Tek 14-7A:
[tt]
k = [-As n - tfs(b - bw)] / (d b)
NCMA Tek 14-1B gives the following:
tfs = 1.75 in
tweb = 0.75 in
wblock = 15 + 5/8in
Where:
b = width of section
bw = for partially grouted walls, width of grouted cell plus
each web thickness within the compression zone
|<---->|---S_core
|<------S_grout----->|
So I would do the following:
b = width of section = grout spacing = S_grout
bw = b - b_cores
b_cores = summation of ungrouted core widths
b_cores = N_core x b_core
b_core = width of core = (wblock - 3*tweb) / 2 = 6.688
N_core = number of ungrouted cores
N_core = (S_grout - S_core) / S_core
S_core = spacing of cores = 8"
N_core = ( 8 - 8)/8 = 0 ungrouted for 8" spa
N_core = (16 - 8)/8 = 1 ungrouted for 8" spa
N_core = (24 - 8)/8 = 2 ungrouted for 8" spa
N_core = (32 - 8)/8 = 3 ungrouted for 8" spa
N_core = (40 - 8)/8 = 4 ungrouted for 8" spa
N_core = (48 - 8)/8 = 5 ungrouted for 8" spa
bcores = 2 x 6.688 = 13.375
bw = 24- 13.375 = 10.625
d = middle of 8" wall = 3.8125
n = 29,000,000 / 1,350,000 = 21.48
As = 0.155 sq. in. (1 - #5 at 24" spacing, 0.31 sq. in per bar)
k = (-0.155*21.48 - 1.25*(24-10.625)) / (3.8125*24) = -0.2191
[/tt]
(2) 8" thick wall
[tt]
tfs = 1.75 in
tweb = 0.75 in
wblock = 15 + 5/8in
Where:
|<---->|---S_core
bw = b - b_cores
[/tt]