Interestingly, or inversely, the Empire State building was supposed to be lit but was not. Looks like Con Ed mixed the networks/supply substation around a bit.
Posts to social media showed landmarks in the city without power, including Rockefeller Center, the Empire State building and parts of Times Square.
Here is Murray Hill supplying Fashion and Empire at the time of Hurricane Sandy.
Networks supplied by Murray Hill in 2015. The number of transformers mentioned in the table are those with PQ monitoring, not the total number in the substation or network.
Murray Hill fed by Vernon at the time of Sandy.
The blue line represents 5 138kv feeders originating from Vernon supplying East 40th st and Murray Hill substation.
If wondering Queens bridge takes 138kv and steps it down to 69kv with 7 69kv feeders supplying East 63rd st.
The Vernon double ring bus, which interconnects generation to the 138kv transmission system in Queens.
38M01, 38M03, 38M04, 38M05, 38M06 feed out to 40th st and Murray Hill.
My guess for the numbering (missing 38M02) is that at one point 7 69kv cables fed out but were upgraded to 5 138kv cables.
If I have it right 38M72 is no longer "capped off" (alive on back-feed) but connected through a phase angle regulator were some power can be exchanged between West 49th 138kv and Vernon.