Hi guys,
I need your opinion in the following issue.
I have implemented a project with one LV Generator (3phase, 1900 KVA - 400 Volts - 50 Hz - Star Connection Solid grounded) working in parallel to the Grid (20 kVolts - Star Connection - Solid Grounding).
Generator is connected parallel to the grid using a two windings step up transformer (2500 KVA - Ynd - 0,4/20kV , Solid Grounded).
My customer wants me to prove that Solid Grounding used for the above mentioned Generator is not dangerous to destroy the generator, meaning that in case of a Short Circuit at Generator terminals (LV 400 Volts), generator must be able to withstand the short circuit fault current fed both by Generator and Grid, till protection devices on the generator LV side to work and isolate the fault (sub transient state) from generator terminals.
Generator Manufacturer (Stamford) has advised the attached "thermal damage curve" but this curve doesn't go bellow 2 seconds, and as Stamford advised there is not such a curve bellow 2 seconds.
The Short Circuit study made according to IEC909 and has come to these results:
3phase Bolted Short Circuit Total Fault Current : 72,4 kA
1phase to Ground Short Circuit Total Fault Current: 86,4 kA
I would like to have your comments on the grounding method of this generator. I mean, do you think that generator is capable to withstand the above faults for i.e 1 or 0,5 seconds?
PS : For sure using an earthing resistor (or reactor) on the star point of the generator would result in much more lower fault currents (Single Line to Ground Fault) but the installation is completed and i want to avoid modifications.