Hi Mbrooke,
There is a good argument (in my opinion) for automatically tripping
the breaker when the stage 2 (low low) density is reached.
Regardless of what action is taken for low gas, the manufacturer must
ensure that the breaker can safely interrupt at the stage 2 density.
All practical gas leaks are slow leaks, which means that the moment when
the densimeter announces stage 2 is the last moment to safely open the
breaker. When the densimeter reaches stage 2, two actions are possible:
(1) Lock out all trips, because tripping after *passing* stage 2 is dangerous.
(2) Trip immediately.
I favour option (2) because:
- It avoids low gas blocking circuitry which must affect both A and B trip
circuits. Consider how much expense and effort goes into redundant
protection, only to have both protections blocked by a (usually) single
densimeter and cheap auxiliary contactor. Densimeters are often not
maintained, tested, etc.
With a tripping strategy, you can just operate the B trip circuit and
leave A clean and independent.
- Recovering from a "locked out" condition often means de-energising the
bus. In some cases (bus section breakers) it may be necessary to interrupt
two buses. Where I work, the network arrangement allows tripping of one
breaker without major consequence. Opening several is often not convenient.
Note that the stage 2 density is only ever reached when a stage 1 alarm has
been ignored. Automatic tripping action leaves the breaker in a safe state.
Breaker manufacturers like to lock out on low gas because that is the safest
thing for their circuit breaker (and it's associated warranty). I argue that
tripping is usually the best option for the network owner.
Thanks,
Alan