DrDrreeeaaa
- Apr 25, 2008
- 266
Hi all, hope you're well.
I have been tasked with determining the cause for low insulation resistance in a utility scale PV system (2.5MW per inverter, 255x10kW strings per inverter, tens of inverters, and ~1000VDC operating voltage). The inverters are transformerless and the PV field operates ungrounded at all times.
The insulation reduces significantly with increasing humidity and lower temperature (as is typical) - the reduction is significant and can bring the IR down from ~500kOhm to less than 5kOhm per inverter. The installation has some damaged connectors between the PV modules - some are cracked and moisture ingress occurs into some of the connectors.
I am trying to determine the chances that damaged connectors are the cause of the extremely low IR readings. The connectors are nowhere near any bonded metalwork (they are atleast 10cm away), so I am finding it hard to believe that there could be current flow between the connector and the bonding system - except for one possibility - if the connectors and cabling were coated with moisture then it is theoretically possible for current flow to occur from the contact inside the connector, through the moisture layer to the outside of the connector, and then continuing through the moisture layout on the outside of the connector and cable all the way back to the nearest support post for the cable which would be ~20cm away which is grounded metalwork.
This is the only way I could conceive of the damaged connectors causing this issue. Can anyone provide any assessment of the potential for the above 'moisture path' to cause the low IR readings observed? The voltage used for the IR test is approximately 1000VDC as you would expect.
