Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations JAE on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Load Dispersion

Status
Not open for further replies.

normm

Structural
Joined
Jan 29, 2008
Messages
74
Location
GB
I am having a discussion with some friends as to what is the correct method of dispersing a point or line load effects on to structural slab member. The opinions expressed are as follows :

1. You can distribute the load at 45 degrees through floor finish only to the top surface of the slab.
2. You can distribute it at further 45 degrees to the centroid ie midpoint of the slab.
3. You can distribute it still further at 45 degrees to the bottom reinforcement level of slab.

Your opinions and any references you may give will be much appreciated.
 
It depends what your designing.

If you are designing structural slab steel, then the top of the slab is appropriate.

If you are checking beam or punching shear in the slab, then the bottom is appropriate.

If you are checking the load to the substrata for a slab-on-grade, then the bottom is appropriate.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 