The strength of corbel is not the only issue to be resolved. You have a load of 10,000# acting at an eccentricity of at least 6" from the center of the wall (I am assuming it is a double wythe with a total thickness of 8"). It is probably more like a 7" eccentricity because the beam rotates and bears more heavily on the inside face of the corbel. The moment applied to the top of wall is approximately 70,000 inch-lbs which creates significant tensile stress in the wall, possibly an unrealistic expectation for hundred year old brick and mortar.
The foundation is likely a non-reinforced strip footing of unknown width, and we have no idea what bearing pressure the soil can sustain. If you are expecting the wall to act as a deep beam to spread the load over a larger length of footing, the wall would be subjected to bending stress.
An additional column could be a good idea, but it may require underpinning if the existing foundation is not adequate or does not extend far enough to accommodate the column base plate.