Hi All, I am working on a 'podium' level design that has columns and walls landing on its slabs and beams from floor above. The entire podium is going to be topped with 4" concrete topping. The columns and walls transfer not just the usual gravity loads but seismic loads that are shown to act in both vertical and horizontal direction. If we assume the lateral (horizontal) loads, at the base of upper story columns & walls, are taken out in diaphragm and therefore beams & slabs only need to be sized for gravity loads plus vertically directed seismic loads; would that be correct assumption? Note that podium is not CIP, so members are typically connected at ends with simple roller or pin type connections. Let me know your thoughts, thanks.